Buderus Hydraulic Box VC0-VW1 vc0 switch doesn't work #1898
Replies: 4 comments 5 replies
-
Please check https://emsesp.github.io/docs/Troubleshooting/#im-missing-certain-data-from-an-ems-device |
Beta Was this translation helpful? Give feedback.
-
Thank you for supporting! I used the function test of the heat pump to test and move the valves and logged the events. First of all VC0 and VW1 are properly connected. When I change VC0 the VC0 valve moves and when I change VW1 (it's called threeway valve in the settings) the vw1 valve moves. The logs are difficult for me to understand but I think I found the interesting events:
VC0:
When I compare these lines to the ones in #892 I see 2 differences: the words thermostat and boiler are written lower case and my lines contain HPSettings3 instead of ? |
Beta Was this translation helpful? Give feedback.
-
Yes, good catch. But this are exactly the bytes we use for the valve detection. After thermostat sends to boiler offset 6 to 01 (and boiler shows full telegram with 01 in offset 6) also emsesp should show 3-way-valve set. If you set the valve via emsesp it's possibe that the thermostat resets it and you do not see an effect.
Log a bit longer an check if the thermostat or another device takescontrol and resets this value. |
Beta Was this translation helpful? Give feedback.
-
Now I have noticed that it only works when the function test of the heater is activated. Then and just then I can toggle the valves manually. I'm afraid the heat pump doesn't allow to change the valves by hand, except for the manual unhooking of the motor and switching directly at the valve. |
Beta Was this translation helpful? Give feedback.
-
Hi,
I have a Buderus WLW196i heatpump and use a BBQKees Gateway V2 to integrate it into my Home Assistant system. The heating system also has a threeway valve called 'Hydraulic Box VC0-VW1' with the two valves vc0 and vw1. It's this one:
In Home Assistant is a switch called 'switch.boiler_vc0valve' but it unfortunately doesn't work. It's always off. When the valve changes its position to heat up water, the switch remains at off. And when I manually click the switch, the valve does nothing.
I checked the log when using the vc0 switch in HA. There are no errors or warning, I can't really figure it out but for me there is just one info.
Log:
Systeminfo:
Beta Was this translation helpful? Give feedback.